Inverter Wiring
|
10-22-2008, 01:57
Post: #11
|
|||
|
|||
Inverter Wiring
I can't say how earlier 'bird inverters are set up... On my coach the
transfer switch appears to be integrated with the inverter. The transfer switch selects the inverter if not other 120 VAC is available (from shore power or generator). The inverter 120 VAC output passes through (in my case, with dual inverters) 4 circuit breakers that "protect" the inverter 120 VAC circuits. These CBs are located in a separate spot a short way from the main 120 VAC power distribution panel (in my case, behind a door on the engine bulkhead in the bedroom). It is my understanding that earlier year coaches may have had separate inverters, transfer switches, and chargers -- and many of the earlier inverters had a circuit breaker on the inverter that protected it from overload. Later "inverters" have combined the transfer switch, inverter, and charger in a single unit -- some with on-unit circuit breakers, some that (should) use external circuit breakers, and some with both. However, no matter how your coach is physically wired up, if you plan to add a significant new load (such as a basement freezer that might draw as much as 8 or 10 amps), then it seems like a wise precaution to add a secondary inverter just for that device or upgrade the primary inverter to handle the additional load. Since a freezer has an electric motor, it's probably wise to ensure that you have full sine wave current from the inverter to avoid the potential for motor overheating and less efficient operation (that will eat amp-hours from the batteries). Of course, a dedicated circuit from the inverter to the freezer is wise. I realize that this doesn't actually answer how the transfer between the inverter power and shore power are accomplished. I can only guess that the inverter output is passed to the appropriate circuits following the main 120 VAC distribution panel, leaving it to the transfer switch to keep inverter/shore/generator power separated. Perhaps someone else can explain how BB set up that part of the wiring... Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 aeonix1@... On the road at Edinburg, VA On Oct 21, 2008, at 12:53 PM, Gregory OConnor wrote: > Pete, there is a group of switches that stand between the 120V > electric panel and the receptical/appliance. when you power on the > inverter I believe the inverter sends 12volts to the On On switch > and removes shore/gen 120v (what ever the transfer switch is sending) > and paths the power from the inverter.ON1= shore/gen ON2=inverter. > If the switch fails one of the inverterpowered paths wont switch > between the two choices > > Wierd thing is I cant seem to understand how the > receptical/appliance is then protected. The power no longer rus thru > the houshhold style pandnel breaker box but goes directly from the > inverter total output source. I guess any leg once powered by > inverter then has the ability to draw 12.5 amps (or 30 amps if the > individual inverter is a 3600watt). would be good to understand the > protection of circuit wires when you add a larger inverter and more > demand. > Greg94ptCa > > --- In WanderlodgeForum@yahoogroups.com, Pete Masterson > >> >> The inverters in a BB are set up with their own distribution > wiring >> (separate from the main 120 vac panel). So, follow the output > wires >> from the inverter and you should find a distribution system > (possibly >> with circuit breakers) somewhere nearby. You can 'join' a new > wire >> there (or set up an additional circuit breaker) to run to the >> location of the freezer. >> >> Load: you first need to determine what the general load on the >> inverter is at present. What devices are attached and how many > are >> used at the same time? It may be that all the available load is >> (potentially) used up by the existing appliances. >> >> Appliances almost always have watt or amp ratings on them (usually > on >> a tag by the manufacturer's name on the back). To ease > calculations, >> convert all ratings to either watts or amps. (Amps x volts (120) > = >> watts or Watts divided by volts (120) = amps) So, a 1500 watt >> inverter can handle about 12.5 amps in total. You should leave a >> couple hundred watts (2 amps or so) "free" to allow for > calculation >> errors and electrical efficiency. Motors (which don't "like" > certain >> types of inverters) prefer "true sine wave" power -- something an >> older inverter may not provide. Motors (the freezer compressor) > also >> draw as much at 50 more power at start up than their rating, so >> allowance must be made for that, as well. >> >> In all probability, the inverter on your coach is already wired up > to >> use most of its maximum rated power for the appliances already >> attached. I expect, depending on the size of the freezer, that > you >> will find that it draws anywhere from 6 to 8 amps up to around 10 >> amps. (Remember to add for the brief overload for motor start up.) >> >> So, the solution(s) are (1) upgrade the existing inverter from a > 1500 >> watt unit to a 2500 watt, true sine wave unit or (2) add a second >> inverter of about 1000-1500 watts (depending on the size of your >> freezer) to handle only the freezer circuit. >> >> Keep in mind that the additional 'juice' required for the > inverter >> will come at the expense of the batteries. If you only use the >> freezer/inverter while on the road, the engine alternator should > be >> replenishing the house batteries to offset the load, but while >> parked, the house batteries will need to provide the inverter > power, >> and I know from personal experience (I have a home-style 22 cu ft >> side-by-side refrigerator-freezer) that refrigeration can draw > down >> batteries rather quickly. You may need to consider adding > additional >> house batteries (or otherwise increasing the available amp-hours) > to >> compensate for the additional demand. >> >> Pete Masterson >> '95 Blue Bird Wanderlodge WBDA 42 >> aeonix1@... >> On the road at Edinburg, VA >> >> >> >> On Oct 20, 2008, at 8:42 PM, Don Spithaler wrote: >> >>> Guys---I want to set a small freezer in one my outside bays. > There is >>> a plug there but how do I wire it to run off the inverter while > going >>> down the road? How would I know if it will run off a 1500 W > inverter? >>> Thanks >>> Don Spithaler >>> 89 SP 36' >>> Butler, PA >>> >> > > > > ------------------------------------ > > Yahoo! Groups Links > > > |
|||
10-22-2008, 02:22
Post: #12
|
|||
|
|||
Inverter Wiring
On my '87 PT the inverter has its own 15a breaker.
The output of the inverter goes to a relay in the kitchen area (mine was under the sink) that BB calls the 'ice maker relay', but is really the transfer relay. That relay's coil is hooked to either the genny or shore power through the power selector switch. When the relay is not energized the circuts hooked to it are fed from the inverter, when shore or genny power is avaiable the relay picks up and those circuts are fed from that source. HTH, Joe --- In WanderlodgeForum@yahoogroups.com, Pete Masterson wrote: > > I can't say how earlier 'bird inverters are set up... On my coach the > transfer switch appears to be integrated with the inverter. The > transfer switch selects the inverter if not other 120 VAC is > available (from shore power or generator). The inverter 120 VAC > output passes through (in my case, with dual inverters) 4 circuit > breakers that "protect" the inverter 120 VAC circuits. > > These CBs are located in a separate spot a short way from the main > 120 VAC power distribution panel (in my case, behind a door on the > engine bulkhead in the bedroom). > > It is my understanding that earlier year coaches may have had > separate inverters, transfer switches, and chargers -- and many of > the earlier inverters had a circuit breaker on the inverter that > protected it from overload. > > Later "inverters" have combined the transfer switch, inverter, and > charger in a single unit -- some with on-unit circuit breakers, some > that (should) use external circuit breakers, and some with both. > > However, no matter how your coach is physically wired up, if you plan > to add a significant new load (such as a basement freezer that might > draw as much as 8 or 10 amps), then it seems like a wise precaution > to add a secondary inverter just for that device or upgrade the > primary inverter to handle the additional load. Since a freezer has > an electric motor, it's probably wise to ensure that you have full > sine wave current from the inverter to avoid the potential for motor > overheating and less efficient operation (that will eat amp-hours > from the batteries). Of course, a dedicated circuit from the inverter > to the freezer is wise. > > I realize that this doesn't actually answer how the transfer between > the inverter power and shore power are accomplished. I can only guess > that the inverter output is passed to the appropriate circuits > following the main 120 VAC distribution panel, leaving it to the > transfer switch to keep inverter/shore/generator power separated. > Perhaps someone else can explain how BB set up that part of the > wiring... > > Pete Masterson > '95 Blue Bird Wanderlodge WBDA 42 > aeonix1@... > On the road at Edinburg, VA > > > > On Oct 21, 2008, at 12:53 PM, Gregory OConnor wrote: > > > Pete, there is a group of switches that stand between the 120V > > electric panel and the receptical/appliance. when you power on the > > inverter I believe the inverter sends 12volts to the On On switch > > and removes shore/gen 120v (what ever the transfer switch is sending) > > and paths the power from the inverter.ON1= shore/gen ON2=inverter. > > If the switch fails one of the inverterpowered paths wont switch > > between the two choices > > > > Wierd thing is I cant seem to understand how the > > receptical/appliance is then protected. The power no longer rus thru > > the houshhold style pandnel breaker box but goes directly from the > > inverter total output source. I guess any leg once powered by > > inverter then has the ability to draw 12.5 amps (or 30 amps if the > > individual inverter is a 3600watt). would be good to understand the > > protection of circuit wires when you add a larger inverter and more > > demand. > > Greg94ptCa > > > > --- In WanderlodgeForum@yahoogroups.com, Pete Masterson > > > >> > >> The inverters in a BB are set up with their own distribution > > wiring > >> (separate from the main 120 vac panel). So, follow the output > > wires > >> from the inverter and you should find a distribution system > > (possibly > >> with circuit breakers) somewhere nearby. You can 'join' a new > > wire > >> there (or set up an additional circuit breaker) to run to the > >> location of the freezer. > >> > >> Load: you first need to determine what the general load on the > >> inverter is at present. What devices are attached and how many > > are > >> used at the same time? It may be that all the available load is > >> (potentially) used up by the existing appliances. > >> > >> Appliances almost always have watt or amp ratings on them (usually > > on > >> a tag by the manufacturer's name on the back). To ease > > calculations, > >> convert all ratings to either watts or amps. (Amps x volts (120) > > = > >> watts or Watts divided by volts (120) = amps) So, a 1500 watt > >> inverter can handle about 12.5 amps in total. You should leave a > >> couple hundred watts (2 amps or so) "free" to allow for > > calculation > >> errors and electrical efficiency. Motors (which don't "like" > > certain > >> types of inverters) prefer "true sine wave" power -- something an > >> older inverter may not provide. Motors (the freezer compressor) > > also > >> draw as much at 50 more power at start up than their rating, so > >> allowance must be made for that, as well. > >> > >> In all probability, the inverter on your coach is already wired up > > to > >> use most of its maximum rated power for the appliances already > >> attached. I expect, depending on the size of the freezer, that > > you > >> will find that it draws anywhere from 6 to 8 amps up to around 10 > >> amps. (Remember to add for the brief overload for motor start up.) > >> > >> So, the solution(s) are (1) upgrade the existing inverter from a > > 1500 > >> watt unit to a 2500 watt, true sine wave unit or (2) add a second > >> inverter of about 1000-1500 watts (depending on the size of your > >> freezer) to handle only the freezer circuit. > >> > >> Keep in mind that the additional 'juice' required for the > > inverter > >> will come at the expense of the batteries. If you only use the > >> freezer/inverter while on the road, the engine alternator should > > be > >> replenishing the house batteries to offset the load, but while > >> parked, the house batteries will need to provide the inverter > > power, > >> and I know from personal experience (I have a home-style 22 cu ft > >> side-by-side refrigerator-freezer) that refrigeration can draw > > down > >> batteries rather quickly. You may need to consider adding > > additional > >> house batteries (or otherwise increasing the available amp-hours) > > to > >> compensate for the additional demand. > >> > >> Pete Masterson > >> '95 Blue Bird Wanderlodge WBDA 42 > >> aeonix1@ > >> On the road at Edinburg, VA > >> > >> > >> > >> On Oct 20, 2008, at 8:42 PM, Don Spithaler wrote: > >> > >>> Guys---I want to set a small freezer in one my outside bays. > > There is > >>> a plug there but how do I wire it to run off the inverter while > > going > >>> down the road? How would I know if it will run off a 1500 W > > inverter? > >>> Thanks > >>> Don Spithaler > >>> 89 SP 36' > >>> Butler, PA > >>> > >> > > > > > > > > ------------------------------------ > > > > Yahoo! Groups Links > > > > > > > |
|||
10-22-2008, 02:24
Post: #13
|
|||
|
|||
Inverter Wiring
If the freezer is that small, then you shouldn't need to upgrade
anything. Just find a 120 vac outlet (socket) that's already on the inverter (in your basement) and relocate or extend it to reach the spot where your freezer will be placed. 95/120 is > 1 amp so it's not a significant load. However, the concern over sine wave vs. modified sine wave vs. square wave output from the inverter is an issue. If the freezer has a compressor motor, it will run best on true sine wave current. It will (likely) run, but less efficiently, on modified sine wave (the motor will run hotter and draw more current, perhaps 1.5 amps) -- this will cause it to eventually fail sooner than it would if run on true sine wave current. It probably won't run on square wave inverted power. I assume you have a microwave (that works on inverter power) so, you most probably have modified sine wave. You're not at a great risk of overwhelming your inverter with this additional load. BTW, check to see if the freezer actually has a compressor -- there are some small refrigeration devices that use a solid-state device for cooling. They're usually pretty small (and don't draw much power), however they're also much less demanding about the type of wave received on the AC power. (They typically have an internal power supply that turns the electricity back into DC for the solid state device.) Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 aeonix1@... On the road at Edinburg, VA On Oct 21, 2008, at 7:02 PM, Donald Spithaler wrote: > Pete > The freezer that I'm looking at is small. It is 115V / 95W so it > would be drawing under 1 amp. Is that right? I would be only using > the inverter while going down the road. We don't dry camp any. On > the road the only thing on the inverter would be the TV & my > laptop. I'm not ready to upgrade the inverter at this time & I > don't want to get into that unless I have to. > Don Spithaler > 89 SP 36' > Butler, PA > > > On Tue, Oct 21, 2008 at 10:52 AM, Pete Masterson > wrote > The inverters in a BB are set up with their own distribution wiring > (separate from the main 120 vac panel). So, follow the output wires > from the inverter and you should find a distribution system (possibly > with circuit breakers) somewhere nearby. You can 'join' a new wire > there (or set up an additional circuit breaker) to run to the > location of the freezer. > > Load: you first need to determine what the general load on the > inverter is at present. What devices are attached and how many are > used at the same time? It may be that all the available load is > (potentially) used up by the existing appliances. > > Appliances almost always have watt or amp ratings on them (usually on > a tag by the manufacturer's name on the back). To ease calculations, > convert all ratings to either watts or amps. (Amps x volts (120) = > watts or Watts divided by volts (120) = amps) So, a 1500 watt > inverter can handle about 12.5 amps in total. You should leave a > couple hundred watts (2 amps or so) "free" to allow for calculation > errors and electrical efficiency. Motors (which don't "like" certain > types of inverters) prefer "true sine wave" power -- something an > older inverter may not provide. Motors (the freezer compressor) also > draw as much at 50 more power at start up than their rating, so > allowance must be made for that, as well. > > In all probability, the inverter on your coach is already wired up to > use most of its maximum rated power for the appliances already > attached. I expect, depending on the size of the freezer, that you > will find that it draws anywhere from 6 to 8 amps up to around 10 > amps. (Remember to add for the brief overload for motor start up.) > > So, the solution(s) are (1) upgrade the existing inverter from a 1500 > watt unit to a 2500 watt, true sine wave unit or (2) add a second > inverter of about 1000-1500 watts (depending on the size of your > freezer) to handle only the freezer circuit. > > Keep in mind that the additional 'juice' required for the inverter > will come at the expense of the batteries. If you only use the > freezer/inverter while on the road, the engine alternator should be > replenishing the house batteries to offset the load, but while > parked, the house batteries will need to provide the inverter power, > and I know from personal experience (I have a home-style 22 cu ft > side-by-side refrigerator-freezer) that refrigeration can draw down > batteries rather quickly. You may need to consider adding additional > house batteries (or otherwise increasing the available amp-hours) to > compensate for the additional demand. > > Pete Masterson > '95 Blue Bird Wanderlodge WBDA 42 > aeonix1@... > On the road at Edinburg, VA > > > > On Oct 20, 2008, at 8:42 PM, Don Spithaler wrote: > > > Guys---I want to set a small freezer in one my outside bays. > There is > > a plug there but how do I wire it to run off the inverter while > going > > down the road? How would I know if it will run off a 1500 W > inverter? > > Thanks > > Don Spithaler > > 89 SP 36' > > Butler, PA > > > > |
|||
10-22-2008, 03:45
Post: #14
|
|||
|
|||
Inverter Wiring
Pete on the old campers like yours and mine the inverters are not as
intuitive as the solid state thing a ma gigs of todays rv's. Wanderlodge put in a bank of switches outside of the inverter to prove cutting edge. If you look at the KurtFiles CD scan 511pdf you will find a bluprint of how the '95 switches between inverter and shore power. there are a row of switches labeled "circuit 14", 24, 13,28, and 7. I would guess the switches are 12volt tripped by a signal from or lack of signal from the inverter. but carry 120volt to pass. If you have issue with one of the labeled items like the refer not powering up on one of the AltCurrent choices, it could be the switch not making the change over. It appears as if the inverter is powered to items like the refer after the large house style altcurrent circuit breaker panel. to test you could run an item on shorepower and prove that tripping the circuitB would shut it down then remove shore power and run the item on inverter only and trip it at the panel. I think it will stay powered Greg94ptCa --- In WanderlodgeForum@yahoogroups.com, Pete Masterson > > I can't say how earlier 'bird inverters are set up... On my coach the > transfer switch appears to be integrated with the inverter. The > transfer switch selects the inverter if not other 120 VAC is > available (from shore power or generator). The inverter 120 VAC > output passes through (in my case, with dual inverters) 4 circuit > breakers that "protect" the inverter 120 VAC circuits. |
|||
10-22-2008, 06:25
Post: #15
|
|||
|
|||
Inverter Wiring
Greg,
I already discovered that the shore/generator power distribution box doesn't affect the inverters. When my coach is stored, I turn off my (home style) refrigerator _and_ pull the breaker (to turn off the light). I normally have shore power available to keep the batteries charged. I was surprised to notice, after unplugging the shore power, that the light in the refrigerator was on (the inverters kicked in automatically). Fortunately, I'd turned off the refrigerator, so only the light came on. (I keep the door propped open a couple of inches to let the inside fully air out so mildew won't grow in my normally dry climate.) That's how I figured that the inverter power is tied into the circuits it serves downstream from the main distribution panel. I'll have to look at the KurtFiles CD -- I just got my copy a couple of days ago, forwarded to me by my house-sitter -- but working time on my coach is limited while we're on the road. I'm not sure I've run across the switches (circuit 14, 24, etc.) you mention -- but I'm going exploring in the inverter box in the next hour or so.... Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 aeonix1@... On the road at Edinburg, VA On Oct 22, 2008, at 11:45 AM, Gregory OConnor wrote: > Pete on the old campers like yours and mine the inverters are not as > intuitive as the solid state thing a ma gigs of todays rv's. > Wanderlodge put in a bank of switches outside of the inverter to > prove cutting edge. If you look at the KurtFiles CD scan 511pdf you > will find a bluprint of how the '95 switches between inverter and > shore power. there are a row of switches labeled "circuit 14", 24, > 13,28, and 7. I would guess the switches are 12volt tripped by a > signal from or lack of signal from the inverter. but carry 120volt > to pass. > > If you have issue with one of the labeled items like the refer not > powering up on one of the AltCurrent choices, it could be the > switch not making the change over. > It appears as if the inverter is powered to items like the refer > after the large house style altcurrent circuit breaker panel. to > test you could run an item on shorepower and prove that tripping the > circuitB would shut it down then remove shore power and run the item > on inverter only and trip it at the panel. I think it will stay > powered > > Greg94ptCa > > --- In WanderlodgeForum@yahoogroups.com, Pete Masterson > >> >> I can't say how earlier 'bird inverters are set up... On my coach > the >> transfer switch appears to be integrated with the inverter. The >> transfer switch selects the inverter if not other 120 VAC is >> available (from shore power or generator). The inverter 120 VAC >> output passes through (in my case, with dual inverters) 4 circuit >> breakers that "protect" the inverter 120 VAC circuits. > > > > ------------------------------------ > > Yahoo! Groups Links > > > |
|||
10-22-2008, 07:01
Post: #16
|
|||
|
|||
Inverter Wiring
Hence every thing running on inverter is only protected from
over/amp by the minimal size breaker on the output side of the inverter. without reguard to the capacity of that circuit protected on shore/gen by the homestyle circuit breaker. Its a good point to keep inmind when upgrading to a larger inverter. I kinda think the inverter output side breaker is there to protect amp draw from damaging the inverter and not the circuit???? A two amp draw on a fridge proves that new technology with fridges, ac units and other appliances is the way to increase capacity of inverter dry camping over a new larger inverter. I still havent installed a new inverter charger. I want to learn what all the shunt and other confusing crap serves so I can bring the cahrging and using of batteries up to the current times. I also need to find out if the switch in the shorecord bay (charge rate) causes a charging problem with a P/O (previous owner) charger upgrade??????? Greg94ptCa --- In WanderlodgeForum@yahoogroups.com, Pete Masterson > > Greg, > > I already discovered that the shore/generator power distribution box > doesn't affect the inverters. When my coach is stored, I turn off my > (home style) refrigerator _and_ pull the breaker (to turn off the > light). I normally have shore power available to keep the batteries > charged. I was surprised to notice, after unplugging the shore power, > that the light in the refrigerator was on (the inverters kicked in > automatically). Fortunately, I'd turned off the refrigerator, so only > the light came on. (I keep the door propped open a couple of inches > to let the inside fully air out so mildew won't grow in my normally > dry climate.) That's how I figured that the inverter power is tied > into the circuits it serves downstream from the main distribution panel. > > I'll have to look at the KurtFiles CD -- I just got my copy a couple > of days ago, forwarded to me by my house-sitter -- but working time > on my coach is limited while we're on the road. I'm not sure I've run > across the switches (circuit 14, 24, etc.) you mention -- but I'm > going exploring in the inverter box in the next hour or so.... > > Pete Masterson > '95 Blue Bird Wanderlodge WBDA 42 > aeonix1@... > On the road at Edinburg, VA > > > > On Oct 22, 2008, at 11:45 AM, Gregory OConnor wrote: > > > Pete on the old campers like yours and mine the inverters are not as > > intuitive as the solid state thing a ma gigs of todays rv's. > > Wanderlodge put in a bank of switches outside of the inverter to > > prove cutting edge. If you look at the KurtFiles CD scan 511pdf you > > will find a bluprint of how the '95 switches between inverter and > > shore power. there are a row of switches labeled "circuit 14", 24, > > 13,28, and 7. I would guess the switches are 12volt tripped by a > > signal from or lack of signal from the inverter. but carry 120volt > > to pass. > > > > If you have issue with one of the labeled items like the refer not > > powering up on one of the AltCurrent choices, it could be the > > switch not making the change over. > > It appears as if the inverter is powered to items like the refer > > after the large house style altcurrent circuit breaker panel. to > > test you could run an item on shorepower and prove that tripping the > > circuitB would shut it down then remove shore power and run the item > > on inverter only and trip it at the panel. I think it will stay > > powered > > > > Greg94ptCa > > > > --- In WanderlodgeForum@yahoogroups.com, Pete Masterson > > > >> > >> I can't say how earlier 'bird inverters are set up... On my coach > > the > >> transfer switch appears to be integrated with the inverter. The > >> transfer switch selects the inverter if not other 120 VAC is > >> available (from shore power or generator). The inverter 120 VAC > >> output passes through (in my case, with dual inverters) 4 circuit > >> breakers that "protect" the inverter 120 VAC circuits. > > > > > > > > ------------------------------------ > > > > Yahoo! Groups Links > > > > > > > |
|||
10-22-2008, 12:23
Post: #17
|
|||
|
|||
Inverter Wiring
Thanks Greg, Pete & all you guys for the input on the inverter. I'll see if I can get a wire to the bay to run the freezer.
Don Spithaler 89 SP 36' Butler, PA On Wed, Oct 22, 2008 at 3:01 PM, Gregory OConnor <"Gregoryoc@aol.com"> wrote:
|
|||
« Next Oldest | Next Newest »
|